Продолжу выкладывать основные неисправности SINUMERIK-810D,840D.
2-15
© Siemens AG, 2006. All rights reserved
SINUMERIK, SIMODRIVE Diagnostics Manual (DA), 11/2006 Edition
Overview of Alarms 2
Product: , Version: 1.0, Language: eng
2.1 NCK ALARMS
0 No (more) alarm(s) present
Definitions: If the communication (variable service) requests more alarms than currently available in the alarm list,
this alarm is communicated as end-of-program function.
Reaction: No alarm reaction.
Remedy: --
Program
Continuation:
Internal
1000 System error %1
Parameters: %1 = System error number
Definitions: With this alarm, internal alarm states are displayed that, in conjunction with the transferred error
number, provide information on the cause and location of the error.
Reaction: NC not ready.
Channel not ready.
NC Start disable in this channel.
Interface signals are set.
Alarm display.
NC Stop on alarm.
Remedy: Make a note of the error text and contact Siemens A&D MC, Hotline
- Tel 0180 / 5050 - 222 (Germany)
- Fax 0180 / 5050 - 223
- Tel +49-180 / 5050 - 222 (International)
- Fax +49-180 / 5050 - 223
- email techsupport@ad.siemens.de
Program
Continuation:
Switch control OFF - ON.
1001 System error %1
Parameters: %1 = System error number
Definitions: With this alarm, internal alarm states are displayed that, in conjunction with the transferred error
number, provide information on the cause and location of the error.
Reaction: Mode group not ready.
Channel not ready.
Interface signals are set.
Alarm display.
Remedy: Make a note of the error text and contact Siemens AG A&D MC, Hotline (tel./fax: see alarm 1000)
Program
Continuation:
Clear alarm with the RESET key in all channels of this mode group. Restart part program.
Добавлено 19-11-2012 15:11
Overview of Alarms 11/2006
NCK alarms
2-16
© Siemens AG, 2006. All rights reserved
SINUMERIK, SIMODRIVE Diagnostics Manual (DA), 11/2006 Edition
1002 System error %1
Parameters: %1 = System error number
Definitions: With this alarm, internal alarm states are displayed that, in conjunction with the transferred error
number, provide information on the cause and location of the error.
Reaction: Alarm display.
Remedy: Make a note of the error text and contact Siemens AG A&D MC, Hotline (tel./fax: see alarm 1000)
Program
Continuation:
Clear alarm with the Delete key or NC START.
1003 Alarm pointer for this self-clearing alarm %1 is zero
Parameters: %1 = Incorrect alarm number
Definitions: The address (zero pointer) used by the compile cycle manufacturer or by the operating system for selfclearing
alarms is not allowed in the system.
Reaction: Alarm display.
Remedy: Make a note of the error text and contact Siemens AG A&D MC, Hotline (tel./fax: see alarm 1000)
Check setCCAlarm/setAlarm (...) call.
Program
Continuation:
Clear alarm with the Delete key or NC START.
1004 Alarm reaction to NCK alarm incorrectly configured
Parameters: %1 = Incorrect alarm number
Definitions: The alarm reaction configured by the operating system or the compile cycles manufacturer is
incorrect.
Reaction: NC not ready.
Channel not ready.
Interface signals are set.
Alarm display.
Remedy: Make a note of the error text and contact Siemens AG A&D MC, Hotline (tel./fax: see alarm 1000)
Change alarm reaction
Program
Continuation:
Switch control OFF - ON.
1005 Operating system error %1 parameter %2 %3 %4
Parameters: %1 = Operating system error number
%2 = Operating system error parameter 1
%3 = Operating system error parameter 2
%4 = Operating system error parameter 3
Definitions: This alarm indicates that the operating system has detected a serious error.
Reaction: NC not ready.
Channel not ready.
NC Start disable in this channel.
Interface signals are set.
Alarm display.
NC Stop on alarm.
Remedy: Make a note of the error text and contact Siemens AG A&D MC, Hotline (tel./fax: see alarm 1000)
Program
Continuation:
Switch control OFF - ON.
Добавлено 19-11-2012 15:14
Overview of Alarms 11/2006
NCK alarms
2-22
© Siemens AG, 2006. All rights reserved
SINUMERIK, SIMODRIVE Diagnostics Manual (DA), 11/2006 Edition
2100 NCK battery warning threshold reached
Definitions: The undervoltage monitor of the NCK battery has reached the prewarning threshold. This is at 2.7-2.9
V (nominal voltage of the battery is 3.0-3.1 V at 950 mAh).
Reaction: Alarm display.
Remedy: Please inform the authorized personnel/service department. The battery must be replaced within the
next 6 weeks. After this period, the voltage can drop below the alarm limit of 2.4-2.6 V if the RAMs to
be buffered take up a lot of current.
Program
Continuation:
Clear alarm with the Delete key or NC START.
2101 NCK battery alarm
Definitions: The undervoltage monitoring (2.4 - 2.6 V) of the NCK battery has responded during cyclic operation.
Reaction: Alarm display.
Remedy: If the NCK battery is replaced without interrupting the power supply, no data will be lost. This means
that production can continue without taking any further steps. (A buffer capacitor on the NCK holds
the supply voltage for at least 30 minutes and the battery can be replaced within this time even when
the control is switched off).
Program
Continuation:
Clear alarm with the Delete key or NC START.
2102 NCK battery alarm
Definitions: The undervoltage monitoring (2.4 - 2.6 V) of the NCK battery was detected during system power-up.
Reaction: NC not ready.
The NC switches to follow-up mode.
Channel not ready.
NC Start disable in this channel.
Interface signals are set.
Alarm display.
NC Stop on alarm.
Remedy: Please inform the authorized personnel/service department. Pull out the battery/fan unit from the NC
module and replace the battery (type: lithium battery with lead, size 1/2 AA, 850 mAh, min. 3.2 V).
The system must then be reinitialized because it must be assumed that data has been lost in the
buffered RAM during the last power-off phase as a result of insufficient supply voltage (refer to Section
2.2 in the Installation and Start-up Guide for the procedure).
The following data might have been corrupted or entirely lost:
- NC machine data
- Drive machine data
- Option data
- Setting data
- User variable
- Global subroutines
- Cycles and macros, as well as
- PLC machine data
- PLC basic program
- PLC user program, and all
- PLC user data
User data in the NCK and PLC (e.g. tool and workpiece data) that have been altered by the
manufacturing process since the last data backup must be updated manually to match the present
machine status!
Program
Continuation:
Switch control OFF - ON.
Добавлено 19-11-2012 15:16
NCK alarms
11/2006 Overview of Alarms
2-23
© Siemens AG, 2006. All rights reserved
SINUMERIK, SIMODRIVE Diagnostics Manual (DA), 11/2006 Edition
2110 NCK temperature alarm
Definitions: The temperature sensor has reached the response threshold of 60 degrees C +/- 2.5 degrees C.
Reaction: Alarm display.
Remedy: In order to reset the sensor, the temperature must be reduced by 7 degrees C.
Program
Continuation:
Clear alarm with the Delete key or NC START.
2120 NCK fan alarm
Definitions: The fan consists of a 26 V DC motor with electronic commutator (rated speed: approx. 8700 rpm). The
commutator signal is used for speed monitoring, response speed: < 7500 rpm.
Reaction: Alarm display.
Remedy: Please inform the authorized personnel/service department. The unit with the fan and NCK battery
must be replaced.
Program
Continuation:
Clear alarm with the Delete key or NC START.
2130 5V/24V encoder or 15V D/A converter undervoltage
Definitions: A failure has occurred in the power supply (FM357-2) to the encoder (5V/24V) or D/A converter (+/-
15V).
Reaction: NC not ready.
The NC switches to follow-up mode.
Mode group not ready, also effective for single axes
NC Start disable in this channel.
Axes of this channel must be re-referenced.
Interface signals are set.
Alarm display.
NC Stop on alarm.
Remedy: Please inform the authorized personnel/service department. Check the encoder and cable for shortcircuits
(the fault should not occur when you remove the cable). Check the power feeder line.
Program
Continuation:
Switch control OFF - ON.
2140 The actual service switch position forces the SRAM to be cleared at the
next Power On (general reset active)
Definitions: The initialization switch is currently set to overall reset. This means that the module's SRAM is deleted
with the next module reset. The NC data memory is cleared during this operation.
Reaction: NC not ready.
Interface signals are set.
Alarm display.
Remedy: Reset initialization switch to zero.
Program
Continuation:
Alarm display showing cause of alarm disappears. No further operator action necessary.
2190 Hardware plug-in module for communication with the digitizer missing
Definitions: MD $MN_ASSIGN_DIGITIZE_TO_CHAN was used to activate the digitizing function by assigning it
to a channel. The function requires a hardware module (RS422 board plugged into the NCU) for
communication with the digitizing unit. This module was not found when booting.
Reaction: Interface signals are set.
Alarm display.
Remedy: Please inform the authorized personnel/service department. Plug in communications module or
cancel channel assignment.
Program
Continuation:
Switch control OFF - ON.
Добавлено 19-11-2012 15:20
Overview of Alarms 11/2006
NCK alarms
2-24
© Siemens AG, 2006. All rights reserved
SINUMERIK, SIMODRIVE Diagnostics Manual (DA), 11/2006 Edition
2192 No NCU link module exists, MD %1 reset
Parameters: %1 = String: MD identifier
Definitions: An attempt was made to activate the NCU link functionality but the hardware is not available. The MD
was reset. Only occurs with the NCU link system
Reaction: NC not ready.
Channel not ready.
NC Start disable in this channel.
Interface signals are set.
Alarm display.
NC Stop on alarm.
Remedy: Install the hardware module and activate the function again (MD).
Program
Continuation:
Switch control OFF - ON.
2193 'Safety Integrated' is not available for link axis %1.
Parameters: %1 = Machine axis index
Definitions: The "Safety Integrated" function is not available for a link axis. Only occurs with the NCU link system
Reaction: NC not ready.
Channel not ready.
NC Start disable in this channel.
Interface signals are set.
Alarm display.
NC Stop on alarm.
Remedy: Use "Safety Integrated" function for local axes only.
Program
Continuation:
Switch control OFF - ON.
2194 Link axis active and $MN_MM_SERVO_FIFO_SIZE != 3
Definitions: At least one axis is to be distributed via NCU link, then the machine data
$MN_MM_SERVO_FIFO_SIZE must be 3. Occurs only with an NCU link system.
Reaction: NC not ready.
Channel not ready.
NC Start disable in this channel.
Interface signals are set.
Alarm display.
NC Stop on alarm.
Remedy: Set $MN_SERVO_FIFO_SIZE to 3.
Program
Continuation:
Switch control OFF - ON.
2195 Channel %1 axis %2 high-speed punching/nibbling not possible via link
Parameters: %1 = Channel number
%2 = Axis name, spindle number
Definitions: An attempt was made to activate high-speed nibbling or punching for an axis programmed on a
different NCU than the drive.
Reaction: Mode group not ready.
Channel not ready.
NC Start disable in this channel.
Interface signals are set.
Alarm display.
NC Stop on alarm.
Channel not ready.
Remedy: High-speed nibbling and punching is only supported on one NCU.
Program
Continuation:
Clear alarm with the RESET key in all channels of this mode group. Restart part program.
Добавлено 19-11-2012 15:35
Еще раз повтoрю,что"ALARM TEXT" любой машины CNC дает лишь направление поиска проблемы!NCK alarms
11/2006 Overview of Alarms
2-83
© Siemens AG, 2006. All rights reserved
SINUMERIK, SIMODRIVE Diagnostics Manual (DA), 11/2006 Edition
6581 NC user memory full
Definitions: The DRAM file system of the user area is full. The order cannot be executed.
Reaction: Alarm display.
Remedy: Delete or unload files (e.g. parts programs)
Program
Continuation:
Clear alarm with the Delete key or NC START.
6582 NC machine OEM memory full
Definitions: The DRAM file system of the machine OEM area is full. The order cannot be executed.
Reaction: Alarm display.
Remedy: Delete or unload files (e.g. parts programs)
Program
Continuation:
Clear alarm with the Delete key or NC START.
6583 NC system memory full
Definitions: The DRAM file system of the system area (Siemens) is full. The order cannot be executed.
Reaction: Alarm display.
Remedy: Delete or unload files (e.g. parts programs)
Program
Continuation:
Clear alarm with the Delete key or NC START.
6584 NC memory limit TMP reached
Definitions: The DRAM file system of the TMP (temporary) area is full. The job cannot be executed.
Reaction: Alarm display.
Remedy: Increase machine date $MD_MM_DRAM_FILE_MEM_SIZE or switch off the precompilation of
individual or all cycles or, if need be,
delete the files in the TMP area.
Program
Continuation:
Clear alarm with the Delete key or NC START.
6585 NC external memory limit reached
Definitions: The DRAM file system of the external area (execution of the external drive) is full.
The job cannot be executed.
Reaction: Alarm display.
Remedy: Load the files to be executed explicitly into the NCK.
Program
Continuation:
Clear alarm with the Delete key or NC START.
6600 NC card memory is full
Definitions: The NC card file system of the NCK is full. No more data can be stored on the NC card.
Reaction: Alarm display.
Remedy: Delete the data on the PCMCIA card.
Program
Continuation:
Clear alarm with the Delete key or NC START.
6610 Too many files open on NC card
Definitions: Too many files are being accessed simultaneously on the NC card.
Reaction: Alarm display.
Remedy: Repeat the action later.
Program
Continuation:
Clear alarm with the Delete key or NC START.